Is it code compliant to run MI cable and normal feeders conduit and wire on same trapeze rack but on different tiers?
Is the MI for fire pumps or fire alarm? Some of our specs included wording that those applications had to have the cable supported independently from other raceways.Is it code compliant to run MI cable and normal feeders conduit and wire on same trapeze rack but on different tiers?
NoIs the MI for fire pumps or fire alarm? Some of our specs included wording that those applications had to have the cable supported independently from other raceways.
Different wiring methods, including MI cable and conductors in conduit, are permitted on the same trapeze rack or support system, provided each wiring method complies with its specific securing and supporting requirements.Is it code compliant to run MI cable and normal feeders conduit and wire on same trapeze rack but on different tiers?