Nice try epic failYeah and take cars off the road that don't meet current safety standards
Did I get the right emoji for sarcasm?
Nice try epic failYeah and take cars off the road that don't meet current safety standards
Did I get the right emoji for sarcasm?
Now you know thats the same. Not even a little bit you should know better. Just saying. Listen it is what is is .Pedro, let me ask you this:
Given that a 3-wire major-appliance circuit allowed the neutral to do double duty to also ground the appliance (and not the EGC doing double duty as the neutral), and given that a typical 3-wire home service is identical to a 3-wire appliance circuit;
Do you have equal objection to 3-wire services, and believe that there should be a separate EGC?
Yeah that's what I suspectedThe emoji was fine lol
Just the emoji lolYeah that's what I suspected
What is your concern, other than an open-neutral condition?Now you know thats the same. Not even a little bit you should know better. Just saying. Listen it is what is is .
I don't know and they only way to find out is to go back and look at the proposals, substantiations, and panel statements. Those are all available on the NFPA website if you want to look for them, but I have no interest in wasting a couple of hours doing that.So being that they changed probably means that cases were finally cited which proves my previous point. Just saying . Thanks for the info
manufactures helping to write code , what can go wrong? Lol
Open neutral is definitely a issue that comes up, more an EC education issue as others have stated the AHJ is not typically opening up range outlets and inspecting them after they are replaced.What is your concern, other than an open-neutral condition?
No, not allowed to install something new that does not meet the current code, but allowed to continue or reuse something that was code complaint when it was installed.So you are working on an old construction you are allowed to install something thats not necessary the best installation as proven by the code changes.
Where it gets interesting is replacing like for like if an equipment ground is present in the box.No, not allowed to install something new that does not meet the current code, but allowed to continue or reuse something that was code complaint when it was installed.
If the neutral was lost on the line side of the service disconnect what difference would it make if the range was connected to the EGC instead of the grounded conductor?Open neutral is definitely a issue that comes up, more an EC education issue as others have stated the AHJ is not typically opening up range outlets and inspecting them after they are replaced.
There was one incident I herd of recently at a apartment building, built in the 1970's, where the apartments were fed from a typical meter pack, 4-wire feeders to each apartment panel - 4 wire range circuit to each range, the old codes (93 and earlier) allowed the 3-wire range receptacles off a sub panel to ground the frame to the neutral, but the neutral had to be insulated. So EC's here typically ran a 4-wire cable and did not use the ground.
The building lost its neutral during a storm and one of the tenants, a disabled person, got a pretty good shock from her range.
I have herd of a few other such incidents over the years, I dont know of a way they are being tracked or recorded as they are not fires.
The existing installation in question was compliant with the code in effect at the time, as there was a 4-wire SE-R cable with a insulated neutral, however,
Under current code 250.140(B) would not apply to a receptacle replacement, as there is a equipment ground present in the box and the receptacle had been replaced.
So my thought is electricians may be unaware of this subtle wording in 250.140(B) and are replacing like with like, when a grounding means is actually present, so I say its more a education issue.
>the old codes (93 and earlier) allowed the 3-wire range receptacles off a sub panelOpen neutral is definitely a issue that comes up, more an EC education issue as others have stated the AHJ is not typically opening up range outlets and inspecting them after they are replaced.
There was one incident I herd of recently at a apartment building, built in the 1970's, where the apartments were fed from a typical meter pack, 4-wire feeders to each apartment panel - 4 wire range circuit to each range, the old codes (93 and earlier) allowed the 3-wire range receptacles off a sub panel to ground the frame to the neutral, but the neutral had to be insulated. So EC's here typically ran a 4-wire cable and did not use the ground.
The building lost its neutral during a storm and one of the tenants, a disabled person, got a pretty good shock from her range.
I have herd of a few other such incidents over the years, I dont know of a way they are being tracked or recorded as they are not fires.
The existing installation in question was compliant with the code in effect at the time, as there was a 4-wire SE-R cable with a insulated neutral, however,
Under current code 250.140(B) would not apply to a receptacle replacement, as there is a equipment ground present in the box and the receptacle had been replaced.
So my thought is electricians may be unaware of this subtle wording in 250.140(B) and are replacing like with like, when a grounding means is actually present, so I say its more a education issue.
What is a stove?>the old codes (93 and earlier) allowed the 3-wire range receptacles off a sub panel
The three wire circuit for stoves and dryers could only originate in the main panel, not a subpanal.
They could have another Cash For Clunkers. That would be coolYeah and take cars off the road that don't meet current safety standards