I've reviewed the Ontario Electrical Safety Authority (ESA) bulletin 36-16-* and they state
(1) Application of cable insulation levels
The cable voltage rating to be used in a particular installation shall be selected on the basis of the applicable phase-to-phase voltage. In addition to the cable voltage rating, the insulation level shall be suitable for the application in accordance with CSA C68.10. Below is a brief description for the applicability of each insulation level as defined in the Standard.
- Cables with 100% insulation level are applicable to grounded systems provided with protection that will clear ground faults within 1 minute.
- Cables with 133% insulation level may be applied where the clearing time requirements of the 100% level category cannot be met, but there is adequate assurance that the faulted section will be deenergized in a time not exceeding 1 h. This insulation level corresponds to that formerly designatedfor ungrounded systems.
- Cables with 173% insulation level are applicable to systems where the time required to de-energize a grounded section is indefinite.
What sorts of systems would have protection systems that would clear ground faults over 1 min to indefinite time periods?
I've reviewed the Ontario Electrical Safety Authority (ESA) bulletin 36-16-* and they state
(1) Application of cable insulation levels
The cable voltage rating to be used in a particular installation shall be selected on the basis of the applicable phase-to-phase voltage. In addition to the cable voltage rating, the insulation level shall be suitable for the application in accordance with CSA C68.10. Below is a brief description for the applicability of each insulation level as defined in the Standard.
- Cables with 100% insulation level are applicable to grounded systems provided with protection that will clear ground faults within 1 minute.
- Cables with 133% insulation level may be applied where the clearing time requirements of the 100% level category cannot be met, but there is adequate assurance that the faulted section will be deenergized in a time not exceeding 1 h. This insulation level corresponds to that formerly designatedfor ungrounded systems.
- Cables with 173% insulation level are applicable to systems where the time required to de-energize a grounded section is indefinite.
What sorts of systems would have protection systems that would clear ground faults over 1 min to indefinite time periods?