So I have an interesting conundrum. I have a service where the meter is on the detached garage. This is because there is vegetation obstructing installation of the service drop to the house.
The meter supplies two service disconnects. One is in the garage and one is in the house. The location is Chicago. Chicago requires the service disconnect for a house to be located inside the house so I can't put it on the garage and run feeders to the house. 230.40 Ex. 3 lets me have two sets of service entrance conductors.
As currently set up, the neutral is bonded in the meter enclosure (the enclosure come that way by default) and in each service disconnect enclosure. The AHJ does not like it because neutral current flows over the service raceway and the neutral conductor between the house and the garage (which is weird, because this happens in all services in Chicago, and probably most other places where metal raceways are used for the service between the meter and the panel(s)).
Anyway, I am thinking about asking if I can rework the set up as shown below. Isolating the neutral from the meter enclosure is not a violation of C

The meter supplies two service disconnects. One is in the garage and one is in the house. The location is Chicago. Chicago requires the service disconnect for a house to be located inside the house so I can't put it on the garage and run feeders to the house. 230.40 Ex. 3 lets me have two sets of service entrance conductors.
As currently set up, the neutral is bonded in the meter enclosure (the enclosure come that way by default) and in each service disconnect enclosure. The AHJ does not like it because neutral current flows over the service raceway and the neutral conductor between the house and the garage (which is weird, because this happens in all services in Chicago, and probably most other places where metal raceways are used for the service between the meter and the panel(s)).
Anyway, I am thinking about asking if I can rework the set up as shown below. Isolating the neutral from the meter enclosure is not a violation of C