Hey guys, so I have a family member who has a room above their garage, that currently is unfinished ( no sheet rock no insulation). They want to finish it and hang sheet rock, but before they do, they would like to add a few outlets. There currently are no outlets or switches in the room they just have an existing feed in a fan box on the ceiling. I know once you extend an existing non AFCi circuit you have to bring the new extended circuit up to AFCI standards.
I was planning on running new 14/2 from the existing fan box to my first new outlet which will be an AFCI receptacle and then loading out to the other outlets. All of the new devices and new wire would be AFCI protected except the existing feed and the small section of new romex to the first receptacle. Would this be code compliant?
I was planning on running new 14/2 from the existing fan box to my first new outlet which will be an AFCI receptacle and then loading out to the other outlets. All of the new devices and new wire would be AFCI protected except the existing feed and the small section of new romex to the first receptacle. Would this be code compliant?