Project of single family 14,000sqft with calculations for service of 600A what’s the best way you suggest to do this. It’s rare for me to see a single family with 600A, max I’ve seen is 400A. Any suggestions?
 
Hey guys
Project of single family 14,000sqft with calculations for service of 600A what’s the best way you suggest to do this. It’s rare for me to see a single family with 600A, max I’ve seen is 400A. Any suggestions?
Your load calcs came up at 600 amps? Big HVAC loads?
 
Are you sure you're using load calcs and not total connected load?

The simplest answer is CT metering and three (or four) 200a panels.
 