i know this is back to the basics but i'm a little confused.
3 phase 75kva transformer
480v primary
Primary conductor size:
75000/830=90amps
90amps x 1.25=113 amps
2 awg good for 115amps.
Next standard breaker size is 125amp
Can I put #2's on the 125 or do I have to go to 1awg?
I have a feeling i'm not interpreting the next higher standard size breaker rule correctly.