SE44.3k Madness
Whalepod
CA
Hey folks. I've been beating my head against the wall for months on this problem. I have a small commercial system with 2 3ph 208v SolarEdge 43.2k's installed. The type with 3 inverters plugged directly into the Solaredge head unit through their own cabling. I don't think my issues are SolarEdge related, but rather heat related. The entire setup is located inside a semi conditioned electrical room inside a building. It's always warm in here, but it's also never 100deg ambient, it shares a small Mini split with the maintenance closet next door separated by a thin wall.
There are 2 of these inverters feeding a 400a SquareD MLO Load center, each inverter on it's own 150a breaker. 1/0 copper conductors to each inverter, about 5-10 feet from the load center. Load Center is being fed by a fused AC disconnect w/ 350kcmil, to a CT cabinet, eventually going to the point of interconnection on lugs in a GE meterbank extension. Never had any issues at all with any equipment south of the Disconnect, it's just the inverters behind the load center that are tripping breakers. There are 0 other devices other than the inverters installed in the load centers.
Every time the system really ramps up and starts producing, one of the inverters trips one of the 150a breakers. It only does it when the systems are both producing at max or close to it. I thought it could have been undersized AC Conductors, but the 1/0 @75deg C should have enough to handle a 120a max continuous load. I've tried replacing one of the breakers. I've moved the breaker within the load center to a new spot on the bus bar to create more space between 150a feeders. I had a local breaker shop test the breakers and they seem to bench test fine on the instantaneous trip curve, however they couldn't test temp related tripping. I thought about upsizing conductors and moving to a larger ampacity breaker, but the load center is maxed out on a 150a branch circuit breaker so I'm stuck with 150. I've tried isolating the issue to one inverter, I've tried isolating the issue to one specific breaker, none of it seems to follow any pattern. I've disassembled the lugs on the breakers and cleaned everything and reassembled. I've meggered the PV AC conductors and they're in great shape. Looking at SolarEdge logs the voltage/current/frequency all look great, until one of the units just shuts off. I've contacted Solaredge tech support and they've looked at the same logs I am and are also stumped.... everything looks great until the breaker just trips. I even got them to replace one of the head units, which didn't effect the issue at all.
Struggling for answers I've turned to thermography. I just picked up a decent handheld IR Camera and tested looking for temp deltas anywhere in the equipment. The system overall was producing about 30% of capacity at the time because of clouds and it being December... but the conductors stayed rock solid at just barely over ambient for as long as I let both inverters run. I'm positive the system will stay on for months in December because it's not producing enough current to heat up the equipment. I'm sure it will tell a different story when it's producing closer to max power, but it was pretty defeating not seeing a smoking gun or really any sort of temp deltas anywhere in the system. The control board was the hottest item in the whole equation at about 90 degrees, so clearly when I was testing heat was not an issue.
Everything in this reads undersized AC conductors to me.... or a high resistance connection somewhere. I just cant find it. I haven't replaced the AC Conductors yet, that may be the last step before throwing up a real hail mary and possibly replacing the load center. FYI I'm using a 1 hole compression lug for AC conductors at the inverter, crimped with a 10ton crimp tool. If it had been a torque or a crimp issue I think I would have seen it on the IR gun.
Anyone have any other ideas at all? I'm totally at a loss here.
Without CT's to monitor supply side of 150A breakers, incorrect phase balancing may add both systems to same leg.
Your diagnostics didn't mention True RMS Amp Clamp of mains, during peak production/ambient, which may be different from on-board CT's.
Your diagnostics didn't mention checking harmonic currents.
Relative to Delta, the WYE xformers amplify current, and circulate harmonics, which may not show up in controller logs.
Thanks for the post!
TRMS Amp Clamp readings with a relatively inexpensive Klien meter on the conductors between the Fused disconnect and the Load center show awfully even current distribution between all 3 phases. We were careful to match L1/L2/L3 from both inverters to the same phase at the load center. My amp clamp readings are awfully close to what's being reported by the inverters.
I didn't check THD though. Could be the next course of action.
From what I understand the Solaredge 4 wire commercial inverters only use the neutral as a voltage reference under normal operation. At the 30% output scenario i tested with the other day there was approx .04A on the neutral at multiple points in the system, with approx 90a on L1/L2/L3 phase conductors. So the neutral really isn't being used here at all, but is brought through the entire system anyway.
An external CT monitoring system watching both inverters and the conductors feeding the load center might be helpful though. I'll kick that idea around.
The 480V SE inverters I have data sheets for show the neutral as optional. I designed many systems using them and I never used a neutral. One thing that could be problematic is that many inverters for which the neutral is optional are shipped with the neutral strapped to ground; if you use a neutral to such an inverter you must remove the strap.
Renting a harmonic-data logger long enough to catch a nuisance trip may be all you need.
I don't think these guys ship with a strap bonding those two together. The bus assembly looks the same on the 480 and 208 versions, but with an extra bolt and pad for the neutral barrel lug. I'll triple check just in case. On the 480's I've installed I've never used a neutral either.
Standard thermal mag CBs, which I am assuming you are using, are calibrated with a trip rating up to 40C ambient and this is the ambient inside the panel around the CBs, not in the room. Over 40C they will trip at a lower and lower current as the temperature increases. Based on your description, and in my experience in similar situations, you are experiencing derated tripping of the CBs under high current high temperature conditions. You need to either reduce the temperature in the electrical room or replace the thermo mags with electronic trip breakers which are less temperature sensitive.
"The system overall was producing about 30% of capacity at the time because of clouds and it being December." Unless this is the condition when the breakers are tripping I would not expect examining the system at this time to reveal anything. You did not find a smoking gun because you did not pull the trigger. ;)
pv_n00b - that's where I'm at too. I haven't been able to dig up a trip curve for the 150a flavor of breaker I'm using, only the 125a version. If I do the math with the 125a trip curve I'm sure i can find the approximate temp that my 150a is tripping.
I thought about upsizing the wire (short runs) and breaker and pull myself out of the thermal trip hell I'm in right now... The problem is that the 150 is the largest breaker available for that panel board, so I would need to replace at least the panel board, but more likely the entire cabinet and both breakers, move to like an SQD I-Line style and be done with it. It's just going to be awfully expensive.
On a scale of 1-10... how would you feel about a cabinet cooling solution? I know they exist, but lord knows I've never actually needed or installed one. I've got plenty of space on the panelboard to wire the circuit easily. Just trying to think of a way to avoid spending 4-6k on replacing all that needs replacing to move to a larger/different breaker style. Spending 1-2k for a cooling solution seems risky, but if it works would definitely be a less expensive fix.
The last one I saw was in a stand alone power panel mounted in the sun at a commercial location. The facilities guy rigged up a sun shade over it and they left the door open and that lowered the heat load enough that it was not tripping until a real solution was found. I lost touch before I heard about what they finally did.
Those little panel AC units do work but it has a price and they will break down before anything else. It's probably a solution, but is it the best? idk.