CT consumption extension
What I said here:
You don't need twisted pair. (I suppose you could make it carefully with a drill if you really had the time and space, but not necessary.)
For 200ft you might want to just use 14awg THHN, as it will give you a little more accuracy and is readily available. I've also used 18awg TFFN lot (stuff I get is crosslisted as MTW so it's fine for wet locations). I've also used that Enphase control cable, which is the same number and guage of conductors.
Just changing the voltage rating of the conductor does not permit you to run what appears to be a Class 2 circuit with line voltage conductors.
I mean that's techically true, but using a Class 1 or higher rated method is fine. So upgrading from something like 300V rated CL3R to 600V THHN does, in fact, permit it.
What I said here:
And yes your post were you talked about that is the same I posted in. First post was very informative
To make a twisted pair that will not try to untwist itself you need to reverse twist the individual wires as you twist the pair.
Retarded question and as soon as you give the answer, I’ll be like oh , but why does the twisting direction matter?
When you twist the pair one way while twisting the individual wires the other way the individual wires are not twisted but just go around each other. If you don't do this the pair will try to untwist itself.
O that if your adding pairs of twisted to a make like a 14-4 twisted pair correct— I can see that
When rope is made they have the same thing to contend with. I have seen rope making machines where the individual twines are twisted one way by planetary gearing while the bundle is twisted the other. This must be done or the rope will come apart every time you cut it.
Are extra long CT wires often part of these installs? Seems like really questionable design choice by enpahse,
In other systems (not related to PV/ESS but used CT's) the CT's have like a short twisted pair 5 amp secondary ~0.333 VAC signal from a CT to a little DIN rail converter box that converts it to industry standard 2-wire loop powered 4-20mA.
output from that converter box goes back the PLC or data logger, your still running shielded cable but its small and manageable like so:
CT --> CT wire (short) --> media converter -> 4-20mA or RS422 long run--> PLC
Just my 2cents enphase should offer direct CT input and 4-20mA or RS422 input or something industry standard like that.
Yeah, I hear you, but it's a trade off I think. For the majority of installs where the combiner is within CT-lead length of the main panel that converter would be an extra cost, extra SKU for logistics (more cost), and extra box on the wall for the customer. (Solaredge was like that last I worked with them, they used a white-labeled WattNode meter and it was more often annoying although sometimes a savior.) It's maybe 10% of installs where CTs need to be extended so they get stuck with slightly lower accuracy in exchange for saving everyone else some margin.
Also on the newest generation product where the meter collar does the consumption monitoring, the functionality you describe is incorporated into the meter collar, so it's an even smaller slice of installs (the partial home backup ones) that might need CT extension. (They're using CAN bus not RS-485, but I don't think that matters to your point.)
Keep in mind this is designed for residential market. In commercial I think the approach you advocate is a no brainer.
Twisted pair for CTs was used in switch gear wiring so the pairs could be traced through out the gear.
There is no practicle reason for making twisted pair when dealing with 5A secondaries.
Enphase says that their comm cable is good for 250 ft. I extended the CT cable using two wires in the comm cable which has a shielded foil in it. I only needed to extend it 25 ft. I ran it in a separate 1-inch conduit with other comm wires in it.
. I grounded the drain wire at one end only.
If running a longer distance, Enphase does not say what to use. I think #10 twisted would work. Also run in a separate conduit. Do not run alongside 240 volt conductors. I decided to keep all the Enphase-supplied wire intact and connected to the wires.
I have not achieved proper operation of my system yet, so can not say if wire extension is functioning.