NEC 110.26(A) Working Space -- Dwelling Unit Existing
brycenesbitt
United States
110.25(A) covers "working space" in front of equipment likely to "likely to require examination, adjustment, servicing, or maintenance while energized "
and generally requires 6 1/2 feet of vertical working space in front.
In my area of older buildings the electrical panels are often in hatches built into the exterior wall.
But we have to the rescue, at least for the smaller buildings:
Exception No. 2: In existing dwelling units, service equipment or enclosed panelboards that do not exceed 200 amperes shall be permitted in spaces where the height of the working space is less than 2.0 m (61⁄2 ft).
That reads "units" not "dwellings". How would you interpret this clause for the set of common meters to a dwelling, not specific to a given unit in that dwelling? Does "dwelling unit" refer to a unit in the dwelling, or to entire buildings?
If a breaker exists in front of the equipment (e.g. it can be turned off but might not actually be turned off) is it still "likely to require examination, adjustment, servicing, or maintenance while energized "?
My take is anything that contains a breaker or fuse is "likely to require examination, adjustment, servicing, or maintenance while energized" no ocpd not likely.
I think the NEC's definition of "dwelling unit" is clear enough. A building can have many dwelling units. My interpretation of the article you quoted is that it applies to any dwelling unit in the building, but not to the building as a whole.
I agree the definition is in Article 100.
NEC 100 Definitions
Dwelling Unit
A single unit, providing complete and independent living facilities for one or more persons, including permanent provisions for living, sleeping, cooking, and sanitation. (CMP-2)
Is there any way to bend this code that to this situation: we have 4 individual unit meters with a unit subpanel, in a 60 inch wide, 2 feet deep hutch on the side of a building. We need to add an additional OCPD to two of the units.
That's easy to do in the hutch and awkward and ugly to do elsewhere.
We can't surface mount the new OCPD because it's a 3 foot zoning district. There is an upstream shutoff so the equipment does not need to be worked on live, in theory.
And the issue is the hutch is less than 6.5ft tall? I'd say there's no argument to make if the AHJ wants to enforce the letter of the code.
Can you mount the new OCPD just behind the doors of the hutch so that that it has the working space outside the hutch? Or flush with doors and modify the doors so they don't cover it up. I think most AHJs are not even persnickety enough to require the latter.
That doesn't cut it. The individual units' equipment is likely to require examination live if, say, you're trying to figure out why unit B lost power and the others didn't and no breakers tripped.
Maybe.
Maybe if I build new doors with an bulge: that way the inside face of the door bulge could be at wall level, with the OCPD case up against it.
The problem with the local AHJ's is even if it passes plan check, it does not matter at inspection time., each inspector makes their own rule.
But this creates it's own worse problem. All the OCPD's set 2 feet back from the doors are in a line.
If some of them are 2 feet forward, it makes it harder to get to or service the unchanged OCPDs.