I have car charger that draws 45A of current 208V single phase with two phase conductor and ground.
If I have two such car chargers and I put all conductors in one conduit then would I need #4 awg or #3 awg copper?
I get #3 awg copper because #4 awg has 70A ampcity and 4 phase conduxtors one conduit i would derate to 70x0.8=56A however my EV charger is continuous then 45x1.25=56.25A thus #3 awg copper.
Am I wrong?