Working at a new facility which is following the IEEE standards of 5ohms or less for the grounding system.
My problem with understanding is when testing why disconnect the rod from the rest of the grounding system? Than won’t you only be reading that one and single rod resistance to earth rather than the whole system?
I can understand the grounding system would need to be isolated away from utility power as you would get super low readings being attached to their MGN. But I can’t understand testing a single rod at a time rather than the whole grounding network resistance to earth.
What value will one rod to earth mean if after test I connected back to a system of 100 rods and Ufer grounds?
Or will the rest of the grounding network while disconnected from rod under test still lower the resistance path back to the single rod.
I just can’t wrap my head around it.
My problem with understanding is when testing why disconnect the rod from the rest of the grounding system? Than won’t you only be reading that one and single rod resistance to earth rather than the whole system?
I can understand the grounding system would need to be isolated away from utility power as you would get super low readings being attached to their MGN. But I can’t understand testing a single rod at a time rather than the whole grounding network resistance to earth.
What value will one rod to earth mean if after test I connected back to a system of 100 rods and Ufer grounds?
Or will the rest of the grounding network while disconnected from rod under test still lower the resistance path back to the single rod.
I just can’t wrap my head around it.