A anbm Senior Member Location TX Occupation Designer Yesterday at 2:37 PM #1 Indoor wiring run, which company makes 2-hr fire rated cables or wires to be used within EMT or RMC conduits and meet NEC 700.10(D)(2)? Doe this cable need to be run inside conduit or can be support/secure somehow inside the bldg.?
Indoor wiring run, which company makes 2-hr fire rated cables or wires to be used within EMT or RMC conduits and meet NEC 700.10(D)(2)? Doe this cable need to be run inside conduit or can be support/secure somehow inside the bldg.?
T tjdilly Member Location Illinois Occupation MEP Engineer - Electrical Yesterday at 3:00 PM #2 Check out Lifeline RHW-2 power cables.
A anbm Senior Member Location TX Occupation Designer Yesterday at 4:00 PM #3 tjdilly said: Check out Lifeline RHW-2 power cables. Click to expand... Need cable size up to 600KCM
T tjdilly Member Location Illinois Occupation MEP Engineer - Electrical Yesterday at 4:10 PM #4 anbm said: Need cable size up to 600KCM Click to expand... Yep, those go up to 750.