spikes2020
Member
- Location
- Nashville, TN
- Occupation
- Electrical Engineer
We have a weird issue, 2 breakers, a feeder in a sub and the main in a panel for some equipment. The feeder breaker is set to 300A ground fault at 0.2 second trip time, while the main in the panel is set to 1200A and 0.1 second. The main panel breaker is tripping first on GF. This is random trips while in operation and there appears not to be any ground faults on the system.
Under further investigation i see that this panel has 30-50% THD on each phase and it is reporting close to 500% TDD. Looking at the harmonics its 3, 5, 7th are crazy high and i assume these are from AC-DC rectifiers, most likely this is from VFDs or power supplies.
This is a 1000A 480V breaker, that most likely feeds several motors (single and 3 phase), plc's, and lots of other equipment. I think they are only pulling maybe 100-150A.
What would be recommended ways to solve this problem? Cap-inductor filters? Isolation transformer? Replace VFDs? Neutral-grounding resistors?