Good point. Some inspectors actual use common sense.While I believe that the code requires a support for a short length, that is not commonly enforced in the field. Check with your AHJ.
Why does that say securing raceway not required within 3' from a coupling? Not sure who wrote that response.At least for emt, 36'' unsupported is legal. Mike holt submitted a PI to allow for a 24" unsupported nipple. CMP says a 36" is already allowed.
Just the title from a short video Mike Holt put out on Instagram, talking about couplings not needing strapped within a certain distance.Why does that say securing raceway not required within 3' from a coupling? Not sure who wrote that response.
I would dispute this. The code doesn't have a definition for secured, however you securely fasten a conduit to a box via a fitting or locknuts. So if you have two boxes within 3 feet of each other, then each box secures the conduit within three feet of a box.Yes it requires a strap or some other type of support. Look at 344.30(A) there is no exception for when the conduit is less than 3' in length. We did have an exception that lasted only one code cycle (2008) for nipples 18" or less but for some reason the geniuses on that CMP removed it.
If the first strap were at 10' from the box then according to your logic the connector is supporting the box within 3'. That's not what the NEC requires.So here's the thing: if the two boxes are less than 3ft apart, then as long as each connector securely fastens the raceway, each end is securely fastened within 3ft of the other box.
Not if the first conduit termination is excluded by implication but any other secure fastening within 3ft counts. The CMP agrees with me, FWIW, see post #5.If the first strap were at 10' from the box then according to your logic the connector is supporting the box within 3'.
'secured' to me depends on context of where the conduit is, that would be hard to pin down in a definition. What can be secured well enough in one area may not be good enough for another.I would dispute this. The code doesn't have a definition for secured
You've got that wrong. The wording was added in the 2008 because it was not permitted to have sections of raceway unsupported. They settled on 18" when certain conditions were met.That last sentence tells you that short nipples did not require support prior to the 2008. The section got deleted in 2011, going back to how it was prior to 2008, after a lengthy PI was submitted detailing all of the issues the 2008 change created.
You've got that wrong. The wording was added in the 2008 because it was not permitted to have sections of raceway unsupported. They settled on 18" when certain conditions were met.