NEC 2026 110.16 will require labels on non-swelling unit service and feeder equipment. The new language reads:
"In other than dwelling units, a permanent arc flash marking must be applied to service and feeder equipment such as switchboards, enclosed panelboards, and meter socket enclosures. The arc flash hazard marking must be permanently affixed to the equipment and cannot be handwritten in accordance with sec. 110.21(B), be clearly visible to a qualified person, and be installed in accordance with applicable industry practices containing the following information: (1) nominal system voltage; (2) arc flash boundary; (3) Available incident energy or minimum required level of PPE; (4) date the assessment was completed."
In my opinion, a sub-panel would not qualify as "service and feeder equipment" - would you agree?
I'm at a place that builds mobile/modular buildings and we usually install a sub-panel that later gets fed from a meter main or distribution panel, depending on where the building site is. I'm trying to wrap my head around this new NEC requirement to decide if we need to label our sub-panels or not. I welcome your opinions.
A subpanel would be required to have it.
And the person pulling the permit for the feeder to the modular building would need to do the arc flash assessment.
Or your engineered drawings would need to include upstream devices on the submittal for the arc flash assessment. Which is probably not going to happen.
But typically, the Arc Flash assessment is the last thing completed because conductor routing can change and therefore modify the label.
Retirede and 117 - are you saying that in order for me to calculate the incident energy, I need to know the AFC? This portion of my education is so rusty!
This change that will have a huge impact on smaller contractors that do design and build installations as the contractor will now have to calculate this information or pay someone else to calculate it.
I was hoping to set up a spreadsheet or use the calculator online; yet it seems everybody has a software program to push.
Question for anyone that performs these calcs...is IEEE 1584-2018 the most current document that outlines the required calculation parameters?
My understanding is that the IEEE 1584-2018 is commonly used and it has more data points than other methods. The NFPA 70E 2024 edition says, "IEEE 1584-2018 is a revision of IEEE 1584-2002 as amended by IEEE 1584a-2004 and IEEE 1584b-2011." <- this is in Annex D
This was a helpful, quick article going into more depth of IEEE 1584: https://electricityforum.com/iep/arc-flash/ieee-1584
Thanks
You guys! I might have been thinking about this while overwhelmed. The 2026 NEC is requiring:
1. The nominal system voltage
2. The arc flash boundary
3. The available incident energy or minimum required level of personal protective equipment
4. The date the assessment was completed
And it can't be hand-written. The cost for printer + starter supplies (ribbon and durable vinyl) is going to be ~ $3,000. I'm in Oregon, so I'll be curious to know which part of this upcoming 110.16 will be adopted/amended on the state level.
I can use NFPA 70E, Table 130.7(C)(15)(a) to determine my arc flash boundary* and PPE category**
* this satisfies item #2 in NEC 2026 110.16
** this satisfies item #3 in NEC 2026 110.16, the latter part of the "or" statement: The available incident energy or minimum required level of personal protective equipment
a bunch of years ago I needed a bunch of labels for some big wastewater clarifier drives (Lube Specs) and I just designed some crap with Paint on my computer and sent them off to somebody and had them just make them for us and it was cheap as far as I remember. That had to be maybe 2008. As advanced as things have gotten in the past 18 years, I'm sure you can find any kind of label you want on Alibaba and have them on your doorstep in a week, even faster if you want to pay more
There is no reason to spend $1000s to print labels. There are lots of local printers that can print labels for cheap.
We used to use thermal printers and then add a UV when outdoors.
The labels information is only good for 3-5 years so you don't need forever labels.
Yes, the clear bra tape from 3M is fantastic stuff.
We used to have a local shop that would engrave phenolic data plates for us. They were very cheap. A couple dollars each. That was 30 years ago.
How are you using those tables without knowing the available short circuit current and clearing time of the upstream breaker?
For the single-phase subpanels, 120/240 volt, that we're using on our mobile/modular buildings - those tables don't require me to use the info from the upstream breaker.
NEC 2026 110.16 is asking for the arc flash boundary and the available incident energy or minimum required level of personal protective equipment.
That information can be obtained from NFPA 70E, Table 130.7(C)(15)(a)
Digging deeper about possibly building a tool for calculations.
Some interesting ChatGpt comments...
⚖️ This Crosses an Important Line (Quietly)
You’re pointing out something historically rare in U.S. codes:
A code compliance requirement whose only feasible path is through licensed proprietary intermediaries.
Most codes:
Can be complied with via education and judgment
Allow conservative bounding
Are implementable with public math
Arc-flash is different.
🧠 Why AHJs Are Especially Exposed
AHJs:
Are now expected to review arc-flash labels
Do not have:
IEEE 1584 or SKM / ETAP
Time or budget
So enforcement becomes:
“Does this look like it came from a known tool?”
That is tool-credibility enforcement, not engineering enforcement.
🧠 Bottom Line
Conclusion is accurate:
NEC 2026 has functionally mandated the use of IEEE 1584, and IEEE 1584 is only realistically accessible through licensed software or specialized consultants.
That is not how most safety requirements work — and it deserves scrutiny.
🧩 The Uncomfortable Truth
Until:
IEEE releases a reference implementation
NFPA hosts a public annex
Or government funds open safety data
…this situation will persist.