AC\DC
- Florence,Oregon,Lane
- EC
Thank you for the constructive input.
Just changing the voltage rating of the conductor does not permit you to run what appears to be a Class 2 circuit with line voltage conductors.
And yes your post were you talked about that is the same I posted in. First post was very informativeWhat I said here:
Current Transformer or CT wires
And from page 12 is the true recommendation: Consumption meter lead wires can be extended to be installed in panels away from where the lQ Gateway is located. These wires may be extended to a maximum of 1.5 Ohms per wire and 3 Ohms for both wires end to end. Appropriately rated, 0.75 mm2 to 1.5...forums.mikeholt.com
You don't need twisted pair. (I suppose you could make it carefully with a drill if you really had the time and space, but not necessary.)
For 200ft you might want to just use 14awg THHN, as it will give you a little more accuracy and is readily available. I've also used 18awg TFFN lot (stuff I get is crosslisted as MTW so it's fine for wet locations). I've also used that Enphase control cable, which is the same number and guage of conductors.
I mean that's techically true, but using a Class 1 or higher rated method is fine. So upgrading from something like 300V rated CL3R to 600V THHN does, in fact, permit it.
That won't work for your application?I tried best I can get is a cable at 3$ a foot
To make a twisted pair that will not try to untwist itself you need to reverse twist the individual wires as you twist the pair.I suppose you could make it carefully with a drill if you really had the time and space, but not necessary.
Retarded question and as soon as you give the answer, I’ll be like oh , but why does the twisting direction matter?To make a twisted pair that will not try to untwist itself you need to reverse twist the individual wires as you twist the pair.
When you twist the pair one way while twisting the individual wires the other way the individual wires are not twisted but just go around each other. If you don't do this the pair will try to untwist itself.Retarded question and as soon as you give the answer, I’ll be like oh , but why does the twisting direction matter?
When rope is made they have the same thing to contend with. I have seen rope making machines where the individual twines are twisted one way by planetary gearing while the bundle is twisted the other. This must be done or the rope will come apart every time you cut it.O that if your adding pairs of twisted to a make like a 14-4 twisted pair correct— I can see that
Yeah, I hear you, but it's a trade off I think. For the majority of installs where the combiner is within CT-lead length of the main panel that converter would be an extra cost, extra SKU for logistics (more cost), and extra box on the wall for the customer. (Solaredge was like that last I worked with them, they used a white-labeled WattNode meter and it was more often annoying although sometimes a savior.) It's maybe 10% of installs where CTs need to be extended so they get stuck with slightly lower accuracy in exchange for saving everyone else some margin.Are extra long CT wires often part of these installs? Seems like really questionable design choice by enpahse,
In other systems (not related to PV/ESS but used CT's) the CT's have like a short twisted pair 5 amp secondary ~0.333 VAC signal from a CT to a little DIN rail converter box that converts it to industry standard 2-wire loop powered 4-20mA.
output from that converter box goes back the PLC or data logger, your still running shielded cable but its small and manageable like so:
CT --> CT wire (short) --> media converter -> 4-20mA or RS422 long run--> PLC
Just my 2cents enphase should offer direct CT input and 4-20mA or RS422 input or something industry standard like that.
What if you route them in the same enclosure/same raceway as the power/voltage tap wiring?The leads of a CT are low volt, low current. You don't need 600v rating.