Hi, all.
One of our high school projects has a small shed near the main building (separate building). The shed will have a motorized rollup overhead door (208V, 3ph), a couple of light fixtures (277V, but could be 120V if needed), and receptacles (120V) - for a total of 3 circuits. All the voltages required are available in the main building.
I was hoping someone might be able to help me with the following questions:
Edgar
One of our high school projects has a small shed near the main building (separate building). The shed will have a motorized rollup overhead door (208V, 3ph), a couple of light fixtures (277V, but could be 120V if needed), and receptacles (120V) - for a total of 3 circuits. All the voltages required are available in the main building.
I was hoping someone might be able to help me with the following questions:
- Does the shed need its own separate grounding system (with a ground rod, ground bar, and all that) as per 250.32(A), or does the exception there apply, if we simply provide the three circuits from a panel at the main building?
- Does the shed need its own panel as well? It feels like overkill to provide a panel for just a shed.
- If a panel is not required and we can simply provide 3 individual circuits, does 225.31 apply, requiring that each each circuit have its own disconnect?
- Do you have any important tips for the electrical design of sheds?