Power Factor varies from 75 to 250
RThorn
Olympia, WA
Engineer
I have been doing a billing analysis for a facility. I am seeing huge variation in Kvar at a facility that gives me unreliable power factor values. I have not been on site so I am not familiar with their loads.
One month I see 16,320 kwh, 8,280 Kvar, and demand of 88.8 kW. That gives a power factor of 93% which is believable.
Two months later I see 33,360 kWh, 19,680 kvar, and a demand of 78.72 kW. That gives me a power factor of 250%.
Other than the sizing of a capacitor bank, what else should we be looking for?
Thanks
It looks like the problem really started after the utility replaced a meter.
The data i have comes right off of the utility bills. Just double checked every line.
Possibly the issue is with the new meter.
Are you sure that, for example, 8,280 Kvar isn't 8,280 var which would also be 8.28 kVar?
kVAR should be a fraction of kW so the VAR numbers look off by a factor of 1000.
Maybe the new meter is reporting in the wrong unit, reporting VAR as kVAR.
Also you're calculating wrong. Say the VAR is off by 1000, power factor in the first example would be 88.8÷(88.8+8.28)=0.91.
In the second example 78.72÷(19.68+78.72)=0.80.
Also I wouldn't assume the Kw and kVAR numbers come from the same intervals so may not tell you anything accurate about the typical power factor, though they may give you a general idea.
Could be. The Utility bill says kVAR
Sorry, my calcs above are wrong, I forgot the relationship is trigonometric. But what we're saying about the kvar and kW figures seeming to be off by 1000 is still correct.
If off by a factor of 1000 on the kVAR then the PF is unbelievably low. Sounds like a meter multiplier issue yet the kWh looks correct
If the kvars are actually vars then the PF would be quite high, not low. Maybe unrealistically high. But if they are kvars then PF is unrealistically low.
And again, not knowing if the demand (W) and kvar data are from the same time intervals introduces further unknowns.
Could you install independent metering as a reality check?
Also...
By any chance was a solar or other parallel source installed at this facility? That would affect power factor measurements.
The more I look at this the more I think it's not even a simple multiplier/units problem and is something deeper that's wrong with the meter data. Back to post #2.
Assuming each of the lines of data is one month, and assuming constant power over the month, I get:
Month 1: PF = 16.32 / sqrt(16.322+8.282) = 89.2%
Month 2: PF = 33.36 / sqrt(33.362+19.682) = 86.1%
I'm not seeing the issue, I assume kVar and kWh are comparable? I.e. 1 VAR = 1 volt * 1 reactive amp, and 1 Wh = 1 volt * 1 real amp.
Cheers, Wayne
Cheers, Wayne
I don't follow. Var is an instantaneous measurement comparable to W not Wh. sqrt(W²+var²)=VA. I don't see how Wh can be figured into the PF calc here.
Ah, I assumed it was kVar-hrs and the idea was to calculate the power factor if the load were constant power over the month.
If kVar is demand kVar, and kW is demand real kW, I don't see how you can use those to calculate anything, as there is no guarantee they occur at the same point in time.
I also assume demand kW is an apparent power figure, as the utility would charge you for the total current you cause to flow.
Cheers, Wayne
I'd make no such assumption.
Fwiw, per this linkedin post I found there are at least eight ways utilities can charge for poor PF. A kvarh charge and a demand charge in VA are both among them. If I were being charged for varh I'd hope any demand charge would be in W so I'm not paying twice for PF. But only the OP can tell us more about the tariff that applies here.
Today's digital meters are certainly capable of transmitting any of the aforementioned datapoints.
I agree. Power factor is the cosine of the angle opposite to kvar in the power triangle. You need to first calculate kva using the pythagorean equation. Pf is then kva divided by kw. I don't have time now to do the math.
exactly. The PF of 0 is 1.
Thanks
You need to not compare apples and oranges.
The kWH value is meaningless when you are doing PF analysis. This is kW usage over time.
The kVAR and kW demand are the values you would use, but it looks like your kVAR may need a multiplier applied to it. The maximum (best?) value for PF is 1.0, while the least (worst?) Is -1.0. Power systems can begin to act funky in the range of .6 to -.9
I would be looking at an Active Power Factor Correction rather than adding straight capacitors at the building service.
Has anyone looked into the "Power House" active PF correction system from Black Hawk Power? It's controversial on energy savings, but seems widely proven on PFC.
Okay, I guess you're assuming that what's given as kvar is actually kvarh. That might make sense.
I was about to put this.
It is common on Utility metering that the kWH is broken into on peak, off peak, etc. and the KVARH that they charge for is not.
So sometimes you need to add the KWHs of the broken down on peak, off peak, etc. to get the total or use the total KWH to compare to the KVARH.
It is not a worst case PF. It is an average.
in excel:
=cos (atan (kVARH / Total KWH))
Is it possible that the kVAR value they presented to you was at a different "instantaneous" time than the kW demand period? I put "instantaneous" in quotes, because many meters calculate kW demand from 15 min periods of measuring kWh (kWh/4 = kW demand)