If you oversize a pipe going into a junction box do you still size that box to “the biggest raceway”
8 - 500 mcm aluminum and 8 - 250 mcm aluminum
Yes, because the wires could be replaced with larger wires in the future.If you oversize a pipe going into a junction box do you still size that box to “the biggest raceway”