Resistive loads only for this purpose.
I want to calculate the VD on the reduced neutral of a feeder to a remote panel. Imbalance current of 12 amp. #6 cu Hots, #8 cu neutral. Avg of 21375 cm. L1 = 25 amp, L2 = 37 amp, N = 8.
I used 120v and 8 amps with a distance of 100' to come up with 1.21% VD or 1.448 volts.
What am I missing? Seems like I should be taking into the consideration the L-L VD.