The utility has given you fault current for the secondary size of their transformer. You do not need to know anything about their transformer. Use the fault value they gave you as your starting point.Thanks Utility company gave me info on fault current but no size of transformer or impedance to conduct calculation on my side for available fault current.
But also, they often base it on”infinite bus” values on their primary, so I have sometimes found it useful to get them to dig in and tell me the real numbers, because they are sometimes lower than what they give you. Had that happen once when their values came up at 44kA and we had an MCC rated for 42kA. Got the real scoop on their transformer (after a bit of a fight) and it came out to 39kA.The utility has given you fault current for the secondary size of their transformer. You do not need to know anything about their transformer. Use the fault value they gave you as your starting point.
I have never had a utility provide primary side fault data unless the customer was buying power at the MV level.
Yes, they regularly use infinite bus, which is definitely not acceptable for arc flash studies.But, at the design stage, infinite bus will usually future proof your installation.But also, they often base it on”infinite bus” values on their primary, so I have sometimes found it useful to get them to dig in and tell me the real numbers, because they are sometimes lower than what they give you. Had that happen once when their values came up at 44kA and we had an MCC rated for 42kA. Got the real scoop on their transformer (after a bit of a fight) and it came out to 39kA.
Agreed This was a "special case" because the customer had made a mistake in ordering the gear and it was already on site.Yes, they regularly use infinite bus, which is definitely not acceptable for arc flash studies.But, at the design stage, infinite bus will usually future proof your installation.
For the handful of times when it truly is incompatible with existing equipment, you need to fight with the utility. But even then, you do not need to know anything about their system capacity or transformer information.
only of the conductors, if they have given you the fault current at the secondary terminalsCorrect me if im wrong. You need impedance to do calculation after the secondary value they provided right. Looked at bussman example. Just trying this step by step by step.
Not really, as Don said.Correct me if im wrong. You need impedance to do calculation after the secondary value they provided right. Looked at bussman example. Just trying this step by step by step.
But also, they often base it on”infinite bus” values on their primary, so I have sometimes found it useful to get them to dig in and tell me the real numbers, because they are sometimes lower than what they give you. Had that happen once when their values came up at 44kA and we had an MCC rated for 42kA. Got the real scoop on their transformer (after a bit of a fight) and it came out to 39kA.
But do you do when it is kind of close like that and in a couple years or so POCO upgrades things because of growing load in your area and that ends up raising actual available fault current at your site even though you are still on same transformer?Agreed This was a "special case" because the customer had made a mistake in ordering the gear and it was already on site.
Having visions of POCO removing service drop in free air, going from pole-mount to pad mount xfmr, with shorter and larger service latteral.POCO upgrades things because of growing load in your area and that ends up raising actual available fault current at your site
I was talking about if they would happen to make upgrades on primary side of a transformer that remains as is. It won't effect max fault current used to determine secondary equipment ratings if you assumed infinite primary bus in the calculation.Having visions of POCO removing service drop in free air, going from pole-mount to pad mount xfmr, with shorter and larger service latteral.
However, if biger xfmrs with larger design impedance are upgraded on existing-service network, how is fault current increased on same wire?
Roger thatupgradese on primary side ..won't effect max fault current….if you assumed infinite primary bus