Electric range question

cppoly

Senior Member
Location
New York
For a 12.6 kW electric range, using the demand factor in table 220.55, you get 8.4 kW. At 208 volts, this works out to 40.38 amps. I vaguely recall Ryan Jackson discussing that you could drop the fractional requirement for load calculations but not for branch circuits. Are you still putting a 40 amp breaker and 40 amp wire in this instance?
 
The spec says 240 volts but I believe someone had confirmed it would work on 208 volts. Something doesn't seem right based upon the spec.

30" Electric Range Stainless Steel-FCFE3083AS | Frigidaire https://share.google/SU5fkmVVt0GBs9wGx
If operated at 208 volts the current will be much lower than that of a 240 volt oven with the listing of 12.6 KW.
 
The spec says 240 volts but I believe someone had confirmed it would work on 208 volts. Something doesn't seem right based upon the spec.

30" Electric Range Stainless Steel-FCFE3083AS | Frigidaire https://share.google/SU5fkmVVt0GBs9wGx

I found the spec via a different approach, and I agree that something doesn't seem right.

According to the spec it only uses 13A at 240V and requires a 40A circuit.

The 40A circuit I believe; it is only a 30" range. But things seem fishy.
 
If this is dual rated 240/208 volts then it should have two different KW ratings. Since you're using a 208 volt supply you can use the lower KW rating in calculating the size of the branch circuit.
 
I have never seen a 208v only residential range or dryer. Only 240/208. I think that is a good thing. The average user or property manager has no understanding about voltages of range/dryer receptacles. Connecting a 208V appliance to a 240V circuit could be a fire hazard.
 
Connecting a 208V appliance to a 240V circuit could be a fire hazard
It would certainly draw more current and have a much higher output so it could be a hazard. FWIW I ran a 208 volt 7.5v kw garage heater on 240 volts for a decade. :censored:
 