I have a proprietary heater that has three heating elements wired in a wye configuration, each requiring phase voltage of 277 V. Initially I was planning on using a neutral connection at the center point, however running a 4-wire circuit may not be possible or advisable, so I'm trying to evaluate how bad the voltage rise could get in the center with different resistance tolerances for each element. It seems like a simple application of KCL, but I'm hoping someone could double-check my work to make sure I'm not over-simplifying this. Here's what I got (with examples values for resistance):
V1: 277<0 V
V2: 277<120 V
V3: 277<-120 V
V0: x (center point voltage)
R1: 10 Ohms
R2: 9 Ohms
R3: 11 Ohms
Via KCL:
(277<0 - x)/10 + (277<120 - x)/9 + (277<-120 - x)/11 = 0
x = 16.07<93.3 V
Thanks!
V1: 277<0 V
V2: 277<120 V
V3: 277<-120 V
V0: x (center point voltage)
R1: 10 Ohms
R2: 9 Ohms
R3: 11 Ohms
Via KCL:
(277<0 - x)/10 + (277<120 - x)/9 + (277<-120 - x)/11 = 0
x = 16.07<93.3 V
Thanks!