Which code cycle are you referring to?I was looking through the nec and realized something.Why did the NEC add the word TAP in 230.46 when speaking about conductor connections?
Your comment makes no sense, sorryIMO 230.46 should just be deleted. The NEC doesnt need to give you permission to make
The NEC must tell you that you cannot do something or how you must do it. They insert a number of these "you can do this" rules which should not be there. Think of it this way,: if 230.46 were deleted, and you spliced a service conductor, what could an inspector cite as a violation?Your comment makes no sense, sorry
But that section, in its current form, also tells us what type of connections can be used for service conductors. The is more restrictive that the types of connections that can be used for other splices and taps.IMO 230.46 should just be deleted. The NEC doesnt need to give you permission to make splices or taps.
They can tell you which connection can used without calling it tapsBut that section, in its current form, also tells us what type of connections can be used for service conductors. The is more restrictive that the types of connections that can be used for other splices and taps.
But the first sentence of 230.46 imposes no restrictions, it is impossible to violate it. There's a huge difference between "shall be permitted" and "shall only be permitted". That sentence (which is the entirety of 2017 NEC 230.46) could be deleted without effect on the NEC.But that section, in its current form, also tells us what type of connections can be used for service conductors. The is more restrictive that the types of connections that can be used for other splices and taps.
The 2017 had no restriction on the types of devices used. That was added in the 2020 and the 2020 is the edition being used in this thread per post #3. The following was added in the 2020 after that first sentence.But the first sentence of 230.46 imposes no restrictions, it is impossible to violate it. There's a huge difference between "shall be permitted" and "shall only be permitted". That sentence (which is the entirety of 2017 NEC 230.46) could be deleted without effect on the NEC.
Cheers, Wayne
Power distribution blocks, pressure connectors, and devices for splices and taps shall be listed. Power distribution blocks installed on service conductors shall be marked “suitable for use on the line side of the service equipment” or equivalent.
Effective January 1, 2023, pressure connectors and devices for splices and taps installed on service conductors shall be marked “suitable for use on the line side of the service equipment” or equivalent.