Microwave "tapped" off of range circuit conductors
JoeNorm
WA
Kitchen remodel of an original 1956 house. They want to keep the microwave in the same location but are adding a toaster right next to it. I noticed the receptacle for the microwave is pulled off of the range circuit. It's not long, in a metal box, and it's worked for 70 years without issue. But I wonder when it's just time for an upgrade, especially since the toaster will now be sharing the receptacle.
The range wire is all old cloth jacketing. It wouldn't be impossible to replace, but definably will add to the job. Is it even an option to leave that setup in place if I have access?
Is it even an option to leave that setup in place..?
Existing construction was built to code:
210.19(A)(3) Exception 1
Remodels are subject to 210.12(D), and the Dennis Alwon Exception
Be careful not to modify the tap > 6ft, or add outlets, since no AFCI exists > 20A.
Replacing oven tap with #12 home run for microwave would ruin a beautiful thing with the existing design.
I doubt the microwave is 70 years old. Possible but highly unlikely. When they changed the appliance to a microwave is when the code violation occurred and hasn't been fixed.
We haven't been told if the range is 240V or 120V. If 240V, I don't see how that is legal or a tap since there would not be OCP to match wiring and appliance.
In order to make that work, there are several hoops to jump through. Because the OP mentions a receptacle, I'm assuming that this microwave is 120V and <= 15A and cord-and-plug connected.
First, the range circuit has to be 50A, not 40A.
Second, the microwave would have to qualify as a "wall-mounted electric oven." That rules out a portable microwave sitting on a counter, but is plausible if it installed as a built-in.
Third, that section requires that the tap conductors, including "the leads supplied with the appliance" to have an ampacity of at least 20A. So the microwave cord would need to have at least #12 copper conductors.
Lastly, 210.21(B)(3) still applies, as the 50A branch circuit supplies at least two outlets, the "wall-mounted electric oven" and the range. So the receptacle would need to be a 50A receptacle, meaning either a 5-50 (do they exist?) or a 14-50. The microwave cord would need to have the corresponding plug.
As far as I can see, if you satisfy all of the above, the install could be compliant. But I may be overlooking some other provision that would throw a wrench into the works.
Cheers, Wayne
If you wont cite code, please explain why code provided in post #2 wont work?
Two things come to mind
1: We don't know the rating of the circuit for the range
2: IMO, the tap rule is meant to be for another cooking appliance, like a countertop unit, microwave, wall mounted oven. It was not meant for a general receptacle for a microwave, toaster, and whatever you want to plug into it.
Cheers, Wayne
Thanks to Wayn for considering tap conductors on a microwave
Regarding your points with NEC 210.19
Household Ranges and Cooking Appliances, Exception 1.
First:
It appears the language for range circuit "not exceeding 50 amperes," probibits any tap to circuits rated > 50A.
Second:
* Since "wall-mounted electric ovens" are not defined in Article 100, microwaves may rely on permissible interpretation:
-- Range hood microwaves have back-plate mount for walls, and redundant bolts secured thru bottom of cabinet / top of microwave
-- A wall mount shelf, or wall-mount cabinet, supporting a microwave oven, may be indirect wall support that relies on permissible interpretation
* Since article 100 defines counter-mounted cooking unit:
"A cooking appliance designed for mounting in or on a counter and consisting of one or more heating elements, internal wiring, and built-in or mountable controls. (CMP-2)"
-- If no wall mount exists, only microwave dog houses for fancy models using heating elements for steam, or browning, would meet this definition
Third:
* These tap conductors (shall) include any conductors that are a part of the leads supplied with the appliance"
-- So receptacle taps wont work, if cord & plug (appliance leads) wont be included in tap-to-receptacle wiring
-- Any hard wiring may need 105C appliance leads, or cord, listed for 20A ampacity per NEC 405, if cord reaches the tap J-box
Lastly:
* Table 210.21(B)(3) wont allow receptacles on a tap, if rated for smaller tap conductors.
-- Receptacles rated for the larger branch circuit before tap, using RV adapters, may fail to use the same leads from appliance to tap.
It appears any microwave using taps, per NEC 210.19 exceptions, must have:
* Appliance J-box terminals listed for hard wiring, or
* A cord & plug listed for 20A ampacity, and only if long enough for direct splice to larger branch tap
-- If not sold as an appliance whip, cutting off a cord cap may violate equipment listings, per NEC 110.3(B), or rely on permissible interpretation.
-- If fixed appliance whip/cords are available with 20A rating, the disconnect must comply with 422.31(B); panel within sight, or lockable breaker.
So to answer the questions:
The range circuit was 2P 40 amp and the wiring had no equipment ground. The receptacle that the microwave plugged into was tapped with #12 copper in a 4 square metal box.
That said, I was there for half a day today changing all that out. The HO was agreeable to the upgrade and the wire swap went even easier than I expected. Some days work out in your favor.
Thanks for the interesting discussion.