AIC and SCCR are the same thing, like conductors and cabe are the same.
The AIC of a device is immaterial if the SCCR of the equipment it is mounted in is not sufficient.
For some 50 years, NEC 110.09 said OCPD must be rated to interrupt the amount of bolted fault amps at their line side terminals. Over the same time 110.10 has said all electrical equipment must be able to tolerate/withstand the amount of short circuit current that exists, at that part of the circuit, until an upstream OCPD operates.