What can you do if you don't have generator alternator data
binwork91
new york
electrical engineer
What can you do if you don’t have generator alternator data when you need to perform a study for an existing building with an existing generator?
What type of study are you having done?
For short circuits, the normal source utility fault contribution is usually greater than that from any single generator.
For arc flash studies the generator data is often critical. Experienced engineering firms may have enough historical data that they are able to make some assumptions, kind of like estimating a transformer impedance.
Is there a better method? I’m uncomfortable estimating values based only on experience.
I always say, if you are going to guess at the input data, just skip the work and guess at the results also.
However you can also perform multiple studies, using different realistic data, such as from IEEE books, and then try to determine a worst case result.
But I am guessing you want to know if you can make some type of field measurements in order to get the data you are missing.
What size is your generator and what type of study are you performing?
There has to be a name plate on it. Probably all kinds of data plates on components inside. I take it you're not on site?
For the project I am working on, it is 200KW generator, and it is arc flash study.
But when a project need both short circuit and arc flash, it is a headache.
For short circuit, the normal source values will be higher. For arc flash the generator incident energy will be higher, as it is common for small generator fault currents to be below the instantaneous pick up point of OCPDs.
I have never seen the x"d any place other than the generator data sheets, which were often only available from tech support.