It would be a pleasure to work with a firm that does that. I refer you to the entirety of this post. In a nut shell. The plans specified HVAC units that were ordered without substitute. The Electrical was installed with equipment locations as drawn but the wire was substituted to Aluminum, so probably minor resistance difference. The short circuit study was commissioned by us, but was not performed until the equipment was already ordered and the cut sheets were given to our PE for his study. The results are as above. WE are "solving" this (at their expense) because the Engineer will not offer any solution OR take any responsibility.We are an MEP firm and we always review mechanical submittals for electrical compliance. Mis-coordination is the most common form of engineering errors and omissions.