M Master Nater Member Location Midwest Occupation Electrical Magician Yesterday at 1:22 PM #21 assuming 3-phase motor, i'd check to see if you're missing a leg or if the contactor has burnt up one of the contacts. amp each leg with clamp meter.
assuming 3-phase motor, i'd check to see if you're missing a leg or if the contactor has burnt up one of the contacts. amp each leg with clamp meter.
R retirede Senior Member Location Illinois Yesterday at 2:23 PM #22 Master Nater said: assuming 3-phase motor, i'd check to see if you're missing a leg or if the contactor has burnt up one of the contacts. amp each leg with clamp meter. Click to expand... 3 phase with a missing leg is not going to result in any rotation at all.
Master Nater said: assuming 3-phase motor, i'd check to see if you're missing a leg or if the contactor has burnt up one of the contacts. amp each leg with clamp meter. Click to expand... 3 phase with a missing leg is not going to result in any rotation at all.
N NuTech.svcs Member Location Salmon, ID Occupation Contractor, appliance repair Yesterday at 2:43 PM #23 start/run cap? Sent from my SM-S938U1 using Tapatalk