Received drawings to bid on a large scale outdoor resi remodel. Haven't been to site yet. It's obvious to me they haven't considered the electrical load in anyway or got involved with an electrical engineer. I'm having trouble figuring out how to load calc all of this. Here's what theyre getting, this is all outdoors and detached from the dwelling:
I'm assuming they have a regular 200A existing service. I want to say they'll need a 400A service just for the back yard. Obviously not looking for someone to calc this, just where I should start. Would the best approach be to calc each individual structure/component and then just add up the VAs? Doing it that way gives me a total VA of 71,943 with a calculated amperage of 299 not including the pool. Thank you.
- In ground pool. Not part of my scope, another electrician is handling this. Pretty sure equipment will be gas though.
- Detached shed. 2 lights and a few outlets for convenience
- Outdoor kitchen
- 2 small appliance circuits
- Gas grill
- Gas cooktop
- Fridge drawer
- Ice maker
- Mini fridge
- Hot tub
- Detached garage
- Approx 12 lights
- Approx 8 receps
- 2 garage door openers
- 1.5ton 18kw heat pump mini split
- (2) outdoor pergolas (this is where I get concerned over load)
- Total of (8) 5200W 240V hardwired infrared electric heaters. Sized for continuous load, which is very likely they'll have all of these on full blast simultaneously gives me 216A.
- (16) LED lights
- (4) motorized screens
I'm assuming they have a regular 200A existing service. I want to say they'll need a 400A service just for the back yard. Obviously not looking for someone to calc this, just where I should start. Would the best approach be to calc each individual structure/component and then just add up the VAs? Doing it that way gives me a total VA of 71,943 with a calculated amperage of 299 not including the pool. Thank you.