So GC wants 100A brought to each floor(4 floors- 4,5,6,7th floor) from 2nd floor. It's going directly up.
We don't know the calculated load so we are just provide 100A 120/208v panel on each floor
We are getting power for this riser from a 277/480v panel( not sure size but it has enough available power).
The plan is to run a feeder from 480v panel to 112kva xfrmr step down and run feeder to 400A panel( all this in same closet) then run (4) separate 100A MC cables to each floor 100A panel. Guess if sized correctly this makes sense?