ATS layout

blueheels2

Senior Member
Location
Raleigh, NC
Occupation
Electrical contractor
Pricing a generator and they have a 200 amp service with 6 “mains”.

Trying to think of the easiest way to do this but I haven’t done many of these.
Option 1- Set 200 amp ats to the right , set 200 amp breaker in this panel and nipple all branch ckts to a new panel on the right. I believe they make an ats/ panel combo I might could use?

Option 2. Set new meter to left, ats to left and change meter main to exterior panel.

Option 3 - new meter to left and ats, panel combo in place of current meter main.

What would yall do
 

Attachments

  • IMG_0498.jpeg
    IMG_0498.jpeg
    132.5 KB · Views: 17
  • IMG_0497.jpeg
    IMG_0497.jpeg
    117.7 KB · Views: 17
I've seen enough ATS fail that I go this way: Meter with 200A disconnect -> ATS -> Distribution panel.

That ATS will fail before anything else, so make it as simple as possible. I hate the idea of an ATS as part of the panel. The disconnect before the ATS allows you to disconnect POCO power to service the ATS w/o involving the POCO.
 
What Code cycle is involved ?
You might have to entertain 230.85
 
Yep, big Orange has them on their website. That would be a tight fit for the wire.
IDK about the bend on the wire, but I have some recollection of a large Homeline breaker or subfeed kit with lug terminals positioned at 90 degrees as well.

Another thing I have done when a subfeed lug kit does not fit is to do a quick load calc, found that 125 is plenty of breaker for the whole house and fed the transfer switch with a 125 breaker. Or even a 100, then you get to use a smaller transfer switch.
 
IDK about the bend on the wire, but I have some recollection of a large Homeline breaker or subfeed kit with lug terminals positioned at 90 degrees as well.

Another thing I have done when a subfeed lug kit does not fit is to do a quick load calc, found that 125 is plenty of breaker for the whole house and fed the transfer switch with a 125 breaker. Or even a 100, then you get to use a smaller transfer switch.
Yeah, a lot of newer residential services are way oversized. Reduced one 400 amp service to 200, everything was gas, including the heat. Biggest load was two A/C compressors at 20 amp a piece.
 