Can a bond bushing replace an EGC in an electrical update?
dgraham
New User
Austin Texas
I am doing a renovation for a municipal client and most of the conduit is 40+ years old so they used the raceway as a ground. The client and engineer want to know if it is possible for us to use bond bushings in each box instead of pulling in a new EGC.
Welcome to the forum.
For the most part, conduit that is properly connected to metallic boxes and enclosures can act as the EGC without additional bonding.
The raceway is permitted as the EGC. Bonding bushings can be used but are probably not required depending on a few factors like concentric or eccentric KOs and above 250 volts to ground.
FWIW, I always specify a wire EGC. Every joint/connection in a conduit run is a potential point of failure.
And so is every wire nut and screw.
In most commercial construction with metal framing you could leave every raceway joint loose and still have a better EGC than a wire can offer. This is the reason in 517.13 the metallic raceway is the primary EGC and the wire is secondary.
A note about terminology: GEC vs. EGC.
IF you're referring to the green wire that's run with circuits, the pipe itself is quite a good conductor. I've witnessed the UL research tests, where the sloppiest EMT assembly you could ever imagine was able to handle enormous amounts of fault current.
HOWEVER, I've also witnessed (and fixed) a 1963 multi-panel commercial service, where the power company main fed a cluster of three large panels, all grouped together. The extremely competent original contractor - the very man who brought the "Ufer" into the NEC - had counted on the conduit stubs connecting the three panels to 'create' one panel. Alas, nearly half a century later age and corrosion had combined to degrade that ground / neutral bond, resulting in massive power quality problems and voltage surges. Simply isolating the ground from the neutral in two of the panels, and running a green wire to the first panel eliminated the problem.
LIKEWISE, I have discovered that in an ungrounded system (480 3-phase, no neutral), using the pipe alone WILL result in all manner of problems if there are ANY single phase (480 volt 2-wire) circuits. Even a failing light bulb will introduce all manner of transients - and finding that fault is extremely difficult.
I have no problem with redundancy.
100% on the mark, and the fault current should remain somewhere in the direct path of the faulted conductors to the source or OCP.