Does a single receptacle for a sump pump located in an elevator pit need gfci protection? The drawings I have state that the receptacle should be “NON-GFI”
What code cycle is that from? The 2020 added this:
620.6 Ground-Fault Circuit-Interrupter Protection for Personnel.
Each 125-volt, single-phase, 15- and 20-ampere receptacle installed in pits, in hoistways, on the cars of elevators and dumbwaiters associated with wind turbine tower elevators, on the platforms or in the runways
and machinery spaces of platform lifts and stairway chairlifts, and in escalator and moving walk wellways shall be of the ground-fault circuit-interrupter type. All 125-volt, single-phase, 15- and 20-ampere receptacles installed in machine rooms, control spaces, machinery spaces, and control rooms shall have ground-fault circuit-interrupter protection for personnel.
A permanently installed sump pump shall be permanently wired or shall be supplied by a single receptacle that is ground-fault circuit-interrupter protected.
2014. That's the latest I have in PDF. Thanks for the correction.What code cycle is that from? The 2020 added this:
I think they mean readily accessible to the elevator service techs. See this for example:So from the 2020 NEC forward if it is not hard wired it must be a single receptacle with GFCI protection provided most likely with a circuit breaker.
The "sump pump" receptacle is handled separately and is not required to be a "GFCI Receptacle" as the others are. If it were intended to be the same, the section would be worded "A permanently installed sump pump shall be permanently wired or shall be supplied by a single receptacle of the ground-fault circuit-interrupter type."I think they mean readily accessible to the elevator service techs. See this for example:
I disagree with the interpretation in that article. It clearly requires either a single receptacle or hard wired pump. In either case GFCI protection is required. As Roger noted if the GFCI protection is required in the pit then the wording in 620.6 needs to be changed.I think they mean readily accessible to the elevator service techs. See this for example: