I have a buddy who has a property, there are 2 structures the first structure is like an office building with 120/240 single phase power. The second structure is a workshop that has 240V delta with a high leg @208V and no neutral running down to the meter socket. However when you trace the over head service feed @ the first building you see 1 hot continues to the transformer bank without touching the first building (im assuming its the high leg) you see the neutral wire tapped going to the workshop & office building and 2 hots also tapped going to the workshop and office building. It looks like a neutral wire is used to support the cable from pole to pole but its not used as a neutral in the work shop. I hope that makes sense. Im telling him we need to add a delta to wye transformer to get 120v safely from 240v delta. But they were convinced by someone else the neutral is there we just have to bring it down from the pole. Can anyone help me understand what is correct thing to do?