I was replacing a non afci breaker with a afci breaker wire was a 2 wire that came in on the side of the panel.
with the neutral off the buss and hot wire off the breaker I had 120 v to ground on both, unfortunately I found out the hard way
after shutting off other breakers found one on a separate phase when shut off voltage went away. This is a older house
Do you think somewhere in the house these 2 neutrals are crossed ?
thanks Rob