Nuisance tripping

CT1992

New User
Location
Colorado
Occupation
Electrician
Apologies in advance for the long post, but this one has me stumped. I’m a master electrician, I’ve been an electrician for 10+ years and I have dealt with my fair share of nuisance trips, but this one takes the cake. I’m hoping some other electrical nerds might be able to help.

I have a customer that has an outbuilding on her property that she says has several GFCI breakers that are tripping at random times during the day and night. When I say several, I mean like 12-18 different circuits nuisance trip every single day. They aren’t the same circuits tripping every day. It’s a different collection of circuits every day (although some circuits seem to be tripping more often than others, sometimes twice a day). The circuits often trip with no load and it seems like they trip more often at night when no one is working. She says they trip more often when there has been some moisture and when it’s colder. I have also verified much of this myself, I’ve been stopping in here and there for about a week and I’ve noticed the same things.

Now let me give you some background: The panels are located in a horse stable (a very fancy horse stable) that has three separate services feeding it: a 100A genset panel and 2 200A (LS-1 and LS-2) panels. The nuisance tripping for the GFCI breakers is exclusive to the two 200A panels and the place was completed in 2022 - so it’s a virtually brand new building. It’s an Eaton panel with BR series plug on neutral GFCI breakers. The services originate at one pedestal, go underground to vault with AL 350’s in 2 1/2” PVC. Inside the vault, the wires are spliced and then turn into two parallel runs each of 350 aluminum in 2 1/2” HDPE (so no joints) and run 300’ to another vault, are spliced again and converted to 250 copper, and go underground to the stables. There is also a hay barn fed from LS-2 that has 4 GFCI breakers on the sub panel there - these breakers also nuisance trip at the same alarmingly high rate. There is water in the conduits at the lower vault, but I’m not necessarily surprised by that since condensation would have accumulated there. It does also seem that condensation is accumulating in that vault as well.

What I’ve done so far:

- removed the GFCI breaker on two circuits and installed standard breakers with GFCI devices. No nuisance trips on those circuits after.

- replaced the previous breakers with brand new eaton GFCI breakers. These circuits still nuisance trip at the same rate.

- installed two square d breakers in the panel just to see if there was a brand difference on the nuisance trips. These breakers still trip at the same rate.

- verified torquing on all branch circuits, mcb’s and taps

- performed an insulation test on all conductors between the vaults

Anything I’m missing as to why this might be happening and how I can fix it? less
 
What are the loads on these breakers? The length of load side conductors?
Typically, I would not look for line side disturbances first but from experience that does occur. What inductive load is cycling? Have you done any PQ checks? Looking for transient voltage spikes as an inductive load shuts down.
Keying handheld radios have been observed to trip GFCIs.
 
Just a hunch. But with these circuits being underground near a large stable, how deep is this stuff buried and through what kind of soil. Stables always get truck and equipment traffic.

Did you megger the conductors?
 
Check voltage from neutral to ground, and hot to ground at several different points including the panels. Kinda sounds like a failing neutral in the panel feed. Is this off a customer owned transformer? Does the generator fed panel have gfci circuits? If so, it points even more towards a neutral issue.
 
...
They aren’t the same circuits tripping every day. It’s a different collection of circuits every day (although some circuits seem to be tripping more often than others, sometimes twice a day). The circuits often trip with no load and it seems like they trip more often at night when no one is working.

Are there GFCI breakers that have been tripping where you could disconnect both the hot and neutral wires from the breaker output, and it would be OK with the customer for at least a few days? That way, you could see if the capacitance to "ground" of the output wires is necessary for the trips to happen. The rationale for doing this is there could be a spike in voltage on the line side of the breaker, but it might not trip unless there's the capacitance to ground on the load wires that draws a spike in current when there's a spike on the voltage. If it doesn't trip after a number of days with both wires disconnected, try it with only the hot wire connected to the breaker output. And then with just the load neutral wire connected.
 
Are there any kind of activities going on that you can draw a correlation to the tripping? Like washing stalls, or loading out manure with a bobcat, time of day, who is working
 