Can an angle flex connector be used to enter the rear of surface mounted box?

J2H

Member
Location
Wisconsin
Occupation
Broadcast Engineer/Licensed Electrician
Just wondering if it is a violation to use an angle flex connector for something that is surface mounted and can be easily removed, specifically thinking of a Tesla wall connector. It seems to come down to the definition of concealed and is the connector truly concealed.
 
It seems to come down to the definition of concealed and is the connector truly concealed.
I agree, so is it concealed or isn't it? The purpose of this code section is to allow conductors to be pulled into the raceway without removing the equipment.
 
I agree, so is it concealed or isn't it? The purpose of this code section is to allow conductors to be pulled into the raceway without removing the equipment.
That makes sense, if that is the intent of the code section, it would be concealed and would be a violation.
 