nsidebottom
Member
- Location
- Alaska
- Occupation
- EE
I was curious about protection of transformer secondaries. From reading 240.21 (C) (2), I get the impression that the NEC is more concerned with the actual configuration of the transformer as opposed to the actual number of wires coming off of the transformer.
For instance, if I had a transformer where the primary is a single 120V coil, and then I had two separate single-phase coils would that setup still benefit from the exemption from requiring a secondary OCPD? (not split-phase 120/240, but something like you would commonly see in an appliance -- e.x: 120V primary --> 24V secondary (pair of wires) and another separate 60V secondary (separate pair of wires)).
If the answer here is no, what if I was only using one of the secondary coils, so the transformer was being used as a single phase 2 wire in 2 wire out transformer? Whenever I come across a small transformer, they are usually setup in a way to be able to output multiple different voltages by having individual sets of coils with only one of the secondary's being used. It seems like it would be a pain to have to put OCPD's on the secondary conductors in these instances as they are essentially the same as the systems explicitly called out by the NEC as not needing the OCPD.
For instance, if I had a transformer where the primary is a single 120V coil, and then I had two separate single-phase coils would that setup still benefit from the exemption from requiring a secondary OCPD? (not split-phase 120/240, but something like you would commonly see in an appliance -- e.x: 120V primary --> 24V secondary (pair of wires) and another separate 60V secondary (separate pair of wires)).
If the answer here is no, what if I was only using one of the secondary coils, so the transformer was being used as a single phase 2 wire in 2 wire out transformer? Whenever I come across a small transformer, they are usually setup in a way to be able to output multiple different voltages by having individual sets of coils with only one of the secondary's being used. It seems like it would be a pain to have to put OCPD's on the secondary conductors in these instances as they are essentially the same as the systems explicitly called out by the NEC as not needing the OCPD.