If MC cable was allowed and some of these units were above accessible drop ceiling(VAV's) would you use MC cable? They call for conduit which I know technically is NOT EMT but seems to imply it IMO.
If MC is permitted then use that. You equipment schedule seems to imply that there is a separate conduit for each piece of equipment which is probably not the case. For example the VAV's could possibly all be on one circuit, daisy chained together.