Service Conductors vs Service-Entrance Conductors
shieldcracker
San Juan
Per Art 100 Service Conductors begin at the Service Point and end in service disconnecting means. On the other hand Service Entrance Conductors can begin at the Service Point (connecting to a Service Drop/ Lateral), or not (connecting to the Underground/ Overhead Service Conductor), either way per NEC they end at Service Equipment terminals.
Its clear that the lines between a service drop or overhead service conductors and the meter box are indeed Service Entrance Conductors, but what about the lines going out of the meter box to a service disconnect or main breaker loadcenter?
The only mention of the word "meter" in the relevant definitions (basically everything in Article 100 that starts with the word Service) is in "Service Conductors, Underground" as a place that those underground service conductors might terminate. As the service conductors extend all the way to the service disconnecting means, if that disconnecting means is in a separate enclosure from the meter, the service conductors between them are Service Entrance Conductors. If that disconnecting means is in the same enclosure as the meter, then there are no SECs, as per the Informational Note.
In all other cases, the meter is not mentioned in the definitions. So the identity of the service condcutors on the line side and the load side (if any) of the meter are the same. If the meter is on the building with the service disconnecting means (as opposed to, say, on a post 300 feet away at the edge of the property), then the conductors on each side of the meter (barring that underground case above) would be Service Entrance Conductors.
Cheers, Wayne
FWIW, service entrance conductors need to be sized with a 125% factor for continuous loads (barring 100% rated OCPD), while other service conductors do not.
Then perhaps the important distinction here is that Service Entrance Conductors are present in all installations (sized to above) and Overhead/Underground Service Conductors will depend on the actual Service Point location. I suppose the latter are sized to 100% CONT+NCONT because the conductors are mostly outside the building...
Because one end of the service entrance conductors terminate on an OCPD?
Cheers, Wayne
I don't know and have always found the current wording to be confusing and poor. I never really understood the distinction between the two definitions or why we need them both. Just take the different rules and combine them into a single definition.
So there's that.
Cheers, Wayne
I leafed through the NEC2026 and could not find the rule for the other service conductors (OHSC and UGSC) Can you point me in the right direction?
Sent from my SM-G973U using Tapatalk
2026 NEC 230.42(A) has the usual two part criterion where the minimum termination rating (60C or 75C ampacity, no derating) includes a 125% factor for continuous loads. But it covers only Service Entrance Conductors.
Other service conductors are only mentioned in 230.23(A) and 230.31(A) which do not have any 125% factor.
Cheers, Wayne