I have a 3phase transformer that is 1000 feet away from the primary OCPD. The secondary will have its OCPD 30 feet away from the transformer and the secondary System Bonding Jumper (SBJ) will be at the OCPD along with grounding conductor and ground rod. The Code requires an EGC on the primary side and a Supply Side Bonding Jumper (SSBJ) on the Secondary side. Since both the EGC & the SSBJ are attached to the transformer housing doesn't bonding the two grounding systems together create a ground potential between the two?