I have a client who wants to add some loads to a heavily loaded 200A, 240V, single-phase panel. It's an office building, 3200 sq ft.
They want to:
- add a washer and dryer (no idea why)
- a photocopier
- eliminate the break room.
Now, the engineer calculated that the panel exceeds the demand and proposes increasing the service to 400A. This would mean a very large expense for the client because it's practically a new service, a new panel, etc. They asked me what could be done to maintain the 200A service.
We proposed:
- first, eliminate the AC heaters; it's in Florida and they are practically unnecessary.
- Then, eliminate everything related to the break room: disposal unit, microwave, dishwasher, etc. Only the refrigerator remains. These loads are unused and can be eliminated.
The engineer provided some values for the lights and outlets, which I don't know where he got them from, but I followed them.
I proceeded to perform a new load calculation:
Lighting - using the given value of 1500 VA at 100%. Table 220.42
Receptacles: - given value 9800 VA at 100% (<10 kVA). Table 220.44
Washer 1200, Dryer 5800, Photocopier 1000, Fridge 1500: 100%
AC condensers (3 units): I used the MCA from the nameplate. Total 21400 VA at 100%. 440.6(A)
Air handlers (3 units): I used the value from the nameplate of the fans, because the heaters would be eliminated. 4600 VA at 100%.
With all this, I got 198 A. I don't understand how that panel could handle that load if the heaters added 40 kVA. Or am I calculating something wrong?
I have some questions about:
- Are AC units calculated at 100% or is only the largest one considered?
- Are AH units treated as motors, all of them or just the largest? If so, would they be calculated at 125%?
- Are the lights and outlets rated excessively and would require an on-site study or a recalculation based on the NEC?
- How could that panel have been approved with those heaters from the beginning?
- Are there any restrictions on using a service, disconnect, and panel at almost their maximum capacity?
Any help would be greatly appreciated. If possible, which NEC 2020 articles would justify this?
Thank you.
They want to:
- add a washer and dryer (no idea why)
- a photocopier
- eliminate the break room.
Now, the engineer calculated that the panel exceeds the demand and proposes increasing the service to 400A. This would mean a very large expense for the client because it's practically a new service, a new panel, etc. They asked me what could be done to maintain the 200A service.
We proposed:
- first, eliminate the AC heaters; it's in Florida and they are practically unnecessary.
- Then, eliminate everything related to the break room: disposal unit, microwave, dishwasher, etc. Only the refrigerator remains. These loads are unused and can be eliminated.
The engineer provided some values for the lights and outlets, which I don't know where he got them from, but I followed them.
I proceeded to perform a new load calculation:
Lighting - using the given value of 1500 VA at 100%. Table 220.42
Receptacles: - given value 9800 VA at 100% (<10 kVA). Table 220.44
Washer 1200, Dryer 5800, Photocopier 1000, Fridge 1500: 100%
AC condensers (3 units): I used the MCA from the nameplate. Total 21400 VA at 100%. 440.6(A)
Air handlers (3 units): I used the value from the nameplate of the fans, because the heaters would be eliminated. 4600 VA at 100%.
With all this, I got 198 A. I don't understand how that panel could handle that load if the heaters added 40 kVA. Or am I calculating something wrong?
I have some questions about:
- Are AC units calculated at 100% or is only the largest one considered?
- Are AH units treated as motors, all of them or just the largest? If so, would they be calculated at 125%?
- Are the lights and outlets rated excessively and would require an on-site study or a recalculation based on the NEC?
- How could that panel have been approved with those heaters from the beginning?
- Are there any restrictions on using a service, disconnect, and panel at almost their maximum capacity?
Any help would be greatly appreciated. If possible, which NEC 2020 articles would justify this?
Thank you.