I have a kiln with specs saying it runs at 60amps and asks for an 80amp breaker on #4 wire.
I had already purchased #6 copper wiring for this install, which is good to 65 amps. Do I have to follow the manufactures chart on this? I have heard arguments on whether or not kilns are considered continuous loads.
I am in Washington, where they now allow NM to be used with the 75 deg column.
I am not trying to skimp, but also not trying to delay the job if it is not necessary.
Thanks