When to install ground rods for utility pad mount transformer?
choppedslaw
Usa
Journeyman
I’m installing utility pad-mount transformer underground.
Relevant details:
•Spec calls for (2) ¾” x 10’ copper-clad ground rods.
  • Note states: “Install two 3/4” x 10’ copper weld ground rods driven to a minimum depth of 9’-0”.”
  • There is a copper ground bus mounted in the transformer pad window (at finished grade elevation).
  • The rods connect to that ground bus inside the window.
Current site condition:
  • Excavation is approximately 4’ deep below finished grade.
  • Pad/window elevation is at finished grade.
  • Primary and secondary conduits are already installed and and stubbed up from the excavation.
My question is about sequencing and driving elevation:
If I drive the rod from the bottom of the 4’ excavation:
  • Driving 9’ would leave 1’ exposed at the ditch bottom.
  • That would put the rod top 3’ below the pad window.
  • I would not be able to reach the ground bus.
If I drive only 6’ from the ditch bottom so the rod top lands at grade, I would only have 6’ embedment, which does not meet the 9’ minimum driven requirement.
So it seems the only way to both:
  1. Achieve ≥9’ embedment, and
  2. Have the rod top land at the pad window for connection
Is to backfill/bring the area up to near grade and then drive the 10’ rod from that elevation.
Is that the correct interpretation of “driven to a minimum depth of 9’-0”” in this context?
For those who do utility pad-mount work regularly:
  • Do you typically drive rods from finished grade elevation once the pad base is built up?
  • Or is there another accepted method in this scenario?
  • I’m concerned if I backfill then drive rods I run the risk of hitting the installed underground conduits. Primary side is robroy sweeps. Secondary side are pvs 90s.
I want to make sure I meet embedment requirements while also keeping the rod top accessible for connection to the ground bus in the pad window.
Appreciate any insight from those familiar with utility primary installations.