Length of circuit to begin applying voltage drop calculations

A quick calculation tells me that at 200 feet, a 1/0 feeder to a 125 amp panel yields a voltage drop (to the panel) of 5.38%. VD along branch circuits could add another percent or two. That is not good enough. VD is not a myth. Equipment does not operate as well as it should when the applied voltage is low. It is incumbent upon designers and installers to provide our clients with an adequate voltage supply.

Yes, the NEC includes no required maximum amount of voltage drop for the majority of the equipment it covers. It does offer what is essentially a suggestion. But that does not leave us free to ignore VD.
Well said and I'd just add that since the NFPA decided the regulation of voltage drop was not in the scope of the NEC it efforts to regulate it moved to the International Energy Conservation Code (IECC), so its in a adopted code just not the NEC.
And since engineering contracts between a PE and a client typically say the drawings shall "meet all local codes" it could be an 'error or omission' of a PE to not include voltage drop in stamped plans (in CO) where wire sizes are given, as voltage drop is regulated by the state of Colorado IECC section C405.10 in the 2021, which says the total voltage drop across feeders plus branch circuits shall not exceed 5 percent.
While it may not be enforced by the electrical AHJ, it could be enforced down the road by a litigious client as a construction defect ('error or omission' claim) not just the AHJ.
Colorado training materials show that exact commercial requirement but I am not clear on resi. However for residential it depends, Low-rise multifamily, 3 stories or less above grade, is treated under the IECC residential provisions and are likely exempt. DOE's Colorado/IECC materials state that the IECC residential provisions are limited to multifamily buildings that are three stories or less above grade but I'd suggest the OP do submit a RFI and referece IECC section C405.10 or whatever it is at present.
And as Larry correctly pointed out the calculation is based on NEC calculated load of the feeder not panel size.
 
Last edited:
????? Yes, the loads and panels may be single phase, but it is still a 208/120 wye system supplying it. You will still have 208 at the panel, not 240.
its the way its listed that matters. 208Y/120V indicates a 3 phase system where as 120/208V indicates single phase pulled off a 208V 3 phase system.
 
????? Yes, the loads and panels may be single phase, but it is still a 208/120 wye system supplying it. You will still have 208 at the panel, not 240.
But the ANSI methodology is to identify single phase by showing the L-N Low Voltage followed by a slash and then the L-L High Voltage, thus 120/208. Three phase is identified by the L-L High Voltage followed by a Y if the source is a wye, then by a slash and then finally by the L-N Low Voltage (if applicable) For some reason US power companies tend not to follow this methodology.
 
Well said and I'd just add that since the NFPA decided the regulation of voltage drop was not in the scope of the NEC it efforts to regulate it moved to the International Energy Conservation Code (IECC), so its in a adopted code just not the NEC.
And since engineering contracts between a PE and a client typically say the drawings shall "meet all local codes" it could be an 'error or omission' of a PE to not include voltage drop in stamped plans (in CO) where wire sizes are given, as voltage drop is regulated by the state of Colorado IECC section C405.10 in the 2021, which says the total voltage drop across feeders plus branch circuits shall not exceed 5 percent.
While it may not be enforced by the electrical AHJ, it could be enforced down the road by a litigious client as a construction defect ('error or omission' claim) not just the AHJ.
Colorado training materials show that exact commercial requirement but I am not clear on resi. However for residential it depends, Low-rise multifamily, 3 stories or less above grade, is treated under the IECC residential provisions and are likely exempt. DOE's Colorado/IECC materials state that the IECC residential provisions are limited to multifamily buildings that are three stories or less above grade but I'd suggest the OP do submit a RFI and referece IECC section C405.10 or whatever it is at present.
And as Larry correctly pointed out the calculation is based on NEC calculated load of the feeder not panel size.
Thanks for this comment Tortuga, I was unaware of the 5% requirement coming from another code. My question now would be how can you accurately calculate voltage drop on a residence where the load applied is constantly changing? To me, you cant, this is why we perform load calculations and size things the way we do. Commercial and industrial sizing is very different because in those applications the load being served is usually explicitly stated and you know how much certain things will be running. That is never the case in dwelling units, which is why we already oversize them the way we do. Lets be honest here, these apartments will rarely see more than 60-80 amps of load across both phases. The way I see it, in most cases for "Dwelling Units" the voltage drop has already been accounted for with the ammount of VA we apply during our calculations.
 
Thanks for this comment Tortuga. My question now would be how can you accurately calculate voltage drop on a residence where the load applied is constantly changing? To me, you cant, this is why we perform load calculations and size things the way we do. Commercial and industrial sizing is very different because in those applications the load being served is usually explicitly stated and you know how much certain things will be running. That is never the case in dwelling units, which is why we already oversize them the way we do. Lets be honest here, these apartments will rarely see more than 60-80 amps of load across both phases. The way I see it, in most cases for "Dwelling Units" the voltage drop has already been accounted for with the ammount of VA we apply during our calculations.
I don't disagree the load will be very low, and if the building is under 3 stories I don't think the energy code applies, but if the energy code applies the voltage drop calculation is based on the article 220 calculated load for the dwelling unit (I'd use 220.82) and the design voltage is based on 220.5(A). Just be aware it is in the code (may not apply to you) but CYA
 
Lets use real world examples here. These apartments have one heat pump per bed room plus another for the living room, so a 3 bedroom has 4 and a 2 bed has 3. Nice for me the 3 bedrooms are right next to the meter stack so those shouldnt be an issue. So the furthest 2 bedroom is 250' away. The heat pumps are 120V ( dont ask me why🤦‍♂️), the fans are listed to draw 0.4 amps and the compressors are 12.3 amps for a total of 12.7 amps. The MCA is listed as 17A and the Max OCPD is 25 amps (although 20 should be fine). That means even if all 3 of these kicked on at the same time you would see at most 15 amps on one phase and 30 amps on another phase and that would be for a very breif moment before it would go down to nominal ranges or less - Ive seen these same heat pumps typically draw 6-9 amps once running. All that is to say that even if all the heat pumps kick on at the same time it will hardly put a dent in the load capacity.

I'm going to throw a couple of wrenches (some helpful) at the above:
1) By heat pumps, my guess is that they are minisplit systems. If so, there is a good chance that they are inverter fed systems. The running load will probably be less than the MCA most of the time, except for some rare worst case situation. This is good for your installation.
2) If by chance these are _not_ inverter fed systems, then the transient compressor starting current will be considerably larger than both MCA and Max OCPD
3) Since these units are 120V, their impact on voltage drop will be as 120V loads. You don't have the benefit of current canceling on the neutral. So your worst case scenario becomes 30A at 120V when you do your voltage drop calculation.
 
????? Yes, the loads and panels may be single phase, but it is still a 208/120 wye system supplying it. You will still have 208 at the panel, not 240.

This is just a standard naming convention; you have the physics right.

If you have a wye system with 208V L-L and 120V L-N, you call it 208/120V when it is three phases supplied to a panel, and you call it 120/208V when it supplies a single phase. Pot-ay-toe pot-ah-toe :) I've proposed calling 120/208V supplied to a panel 'psingle phase' but that never took off.
 
This is just a standard naming convention; you have the physics right.

If you have a wye system with 208V L-L and 120V L-N, you call it 208/120V when it is three phases supplied to a panel, and you call it 120/208V when it supplies a single phase. Pot-ay-toe pot-ah-toe :) I've proposed calling 120/208V supplied to a panel 'psingle phase' but that never took off.
The NEC trips all over itself trying to describe these systems, I call them open-wye, avoiding wording that implies neutral current canceling.
 