Transformer temperature rise
cppoly
New York
What's the real difference between 115 degree temperature rise transformer compared to a 150 degree temperature rise transformer? Is the only concern heat loss because the full load heat loss difference is only about 100 watts when comparing these two temperature rises using a 45 KVA transformer. Am I missing something?
What destroys transformers is heat. The cooler a transformer runs the longer it lasts.
Heat loss by an indoor transformer is heat that needs to be removed by the HVAC system.
Thanks yes I agree with heat boss but in this case When comparing the heat loss there is only a difference of 100 Watts in heat loss with the 150° Transformer rise. This appears to be very minimal
Yes it does.
For maximum energy saving installs we used to specify 80°C temp rise.
Some time in the early 2000s, the Department of energy determined most small dry typ transformers were only loaded to 35%. This resulted in new requirements for transformer efficiency, which negated some of the difference between 150°C and other designs like 115°C.