I have 100A feeder from Panel A feeding sub panel B all inside town home. Engineer provided #3 awg and using romex. However is that not undersized for 100A breaker since your suppose to use 60C for it?
 
i believe you are correct. NM cable must not be rated any higher than the 60°C column, unless 310.12(B) applies.

i've never seen #3 NM CU cable, but it would have an ampacity of 85a. 240.4(B) allows that feeder to be rounded up to the next size so must be on a 90a OCPD.

310.12(B) allows dwelling feeders to be de-rated by Table 310.12(A), but only in the instance that it feeds the entire load of the dwelling unit. so is the entire sub-panel B feeding an entire "dwelling unit"? if not, this derating does not apply. if so, Table 310.12(A) derating applies, and as small as #4 NM would be sufficient.
 
i believe you are correct. NM cable must not be rated any higher than the 60°C column, unless 310.12(B) applies.

i've never seen #3 NM CU cable, but it would have an ampacity of 85a. 240.4(B) allows that feeder to be rounded up to the next size so must be on a 90a OCPD.

310.12(B) allows dwelling feeders to be de-rated by Table 310.12(A), but only in the instance that it feeds the entire load of the dwelling unit. so is the entire sub-panel B feeding an entire "dwelling unit"? if not, this derating does not apply. if so, Table 310.12(A) derating applies, and as small as #4 NM would be sufficient.

The entire sub panel B does Not feed an entire dwelling unit.
 
The entire sub panel B does Not feed an entire dwelling unit.
then it does not qualify for the Table 310.12(A) derating. there are many folks who think that table applies to any feeder in a dwelling. i know, i was one of them. :) maybe your engineer is one too?
 
then it does not qualify for the Table 310.12(A) derating. there are many folks who think that table applies to any feeder in a dwelling. i know, i was one of them. :) maybe your engineer is one too?
Same applies for the previously mentioned 2AWG aluminum cable, it would only be good for 90 amps if not supplying entire dwelling load.
 
The entire sub panel B does Not feed an entire dwelling unit.
But what is the size of the service or feeder that supplies the entire dwelling unit? If it's 100A, then it and any feeders within the dwelling unit need only have an ampacity of 83A, and 60C #3 Cu would be fine.

Cheers, Wayne
 
But what is the size of the service or feeder that supplies the entire dwelling unit? If it's 100A, then it and any feeders within the dwelling unit need only have an ampacity of 83A, and 60C #3 Cu would be fine.

Cheers, Wayne

The Service that supply the entire dwelling unit is SER and not subject to NEC 2017 Article 340.80. The service is 200A.
 
The service is 200A.
OK, then the 100A feeder needs an ampacity of 100A. Which could be 75C #3 Cu.

So the error here is calling for NM cable, which both doesn't exist in #3, and which would be limited to the 60C ampacity. Use a 75C wiring method, and #3 Cu is the correct size, barring voltage drop concerns.

Cheers, Wayne
 
OK, then the 100A feeder needs an ampacity of 100A. Which could be 75C #3 Cu.

So the error here is calling for NM cable, which both doesn't exist in #3, and which would be limited to the 60C ampacity. Use a 75C wiring method, and #3 Cu is the correct size, barring voltage drop concerns.

Cheers, Wayne

See link below:


If its NM cable and assume #3 awg comes then you amapcity cant be based off of 75C correct based on NEC 2017 Article 340.80?


Sent from my iPhone using Tapatalk
 
this NMD is new to me. i do not find it anywhere in the code book. and it's own spec sheet says the conductors are good for 90°C. not the cable, but the conductors. so, i fail to see the difference between NM-B and NMD. what is the difference and what does the D represent?

edit to add: is it the "damp enclosed location" rating?
 
this NMD is new to me. i do not find it anywhere in the code book. and it's own spec sheet says the conductors are good for 90°C. not the cable, but the conductors. so, i fail to see the difference between NM-B and NMD. what is the difference and what does the D represent?
I think you’ll find that the listing is only CSA, not CSA(US).
 


 