Good evening! I’m just having a bit of a debate at work and was hoping you could help me clear it up. When I have to install my grounding electrodes at residences, I just default to 2 ground rods and then if the house has a ufer I’ll use it or I’ll also use the cold water. And what we are debating is whether you have to run a separate conductor(from main panel) to the ground rods and then another to the water(or ufer). This typically ends with a 6awg from the ground bar to the rods and a 4awg to the water. Or would I be allowed, if I ran #4 from rod to rod and then had my #4 from the water(or ufer), to crimp them together (not in the middle of the rods but at one end or the other of rods, but before they enter the equipment) and then bring only one #4 to my ground bar at my main panel where my main bonding jumper is also located? Thanks in advance!!